mauromartini avatar image

Time delay grid sync

I am needing to add a time delay for a MPii to sync and accept grid power. The scenario is that some gated estates in South Africa require 15-20min delay before inverters are allowed to sync to the grid after a grid failure to stagger and limit power draw on the infrastructure.


I know this is possible and there are a couple of other threads out there but the instructions are not very clear on how to setup the assistants and in what order. We also use ESS and South Africa Grid code.


Thanks!

ESSgrid
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

@Guy Stewart (Victron Community Manager) does not seem like any of the community can help. Have you got any idea how to achieve this? Thanks.
2 Answers
Ingo avatar image
Ingo answered ·

The quick answer is that it's not possible without some external components. The Multi will sync as soon as the grid is seen as 'healthy' enough.

What I had to do is to add a relay and timer to the input side of the Multi with a delay of 20 minutes. This essentially starts the timer as soon as the grid becomes available and after 20 minutes engages the relay to feed power to the Multi. The drawback is that you now have to factor in an additional 20 minutes grid outage time in your battery capacity calculation. EG. If loadshedding is 2H30 and you specified a battery size that just about covers that at X load then you now have to provision capacity for 2H50. If that is not a 'boarder line' case then it's all good and well.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

I think you should be able to use the "programmable relay" and "general flag" assistants to do that.

1642664695364.png

AC IN will be ignored as soon as the grid fails. After grid recovery the timer will start and after 1200s it will stop ignoring the AC IN.

Just give it a try. For testing set the time to 60s or so.


1642664695364.png (52.8 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Will try and let you know.


screenshot-2022-01-20-at-212838.png


@Matthias Lange - DE tried this but no luck. I am running ESS and AC OUT2 when grid fails.

Ok then maybe it is conflicting with ESS.

So you may have to go with the external solution.