herculess avatar image
herculess asked
GX different values grid vs AC loads
My setup actually looks very simple and is just for updates and tests:
1xMultiplus2 5k:
  • AC-IN1 = grid
  • no AC-OUT1/2 connected
  • switch: charger only
PV charger = no PV array connected
no battery connected, PV charger is powered by Multiplus2
to measure grid loads a smartmeter is connected via modbus-tcp.
the problem is, there's a difference between grid L1 and ac-loads L1, but ther shouldn't
L1 ac-loads shows always min. >10W more consumption than the power meter/grid. L2 and L3 show's correct values.
Does someone know the cause of that? the value looks to me calculated, but why and where?
greets
Energy Meter
Alexandra avatar image
Alexandra answered ·
@herculess
One of the phases will have your system self consumption on it most likely.
18W seems about correct for an inverter and gx load. The value is most likely calculated not sure if you are metering both sides?
herculess answered ·
i am just measuring the grid - which includes the self consumption of the inverter/gx etc.
so it is a software issue, that it calculates a value which isn't there.
neco-energies avatar image
neco-energies answered ·
Hello, I have the same problem but more big difference.
Can you help me with that ?
Thank you
ted avatar image
ted answered ·
Same Problem sometimes... Happens in my case with a Dryer if i turn it on1665843819028.png
ted avatar image ted commented ·
I checked the EM24 Phase order, it was L1-L3-L2 in my case. I fixed it, and all measured fine
Stan avatar image
Stan answered ·
I have the same issue, but in single phase instalation.
I found out that voltage measured by MP2 is higher than in ET340 and also than I measured with multimeter. Difference is around +5V.
So maybe this is the issue for incorrect calculation of AC loads.