Multiplus II - will I need an external sensor?

Hi,

my grid connection and main power meter are located on the outside of my house, from which there are two main lines branching off to two different power centrals.

I would like my M+2 to sit in-line between the main meter and one of the centrals, powering all loads on that power central (majority of the building).

Feeding the grid must be avoided.

Would an external sensor be required in this case?

My goal is to only draw power from the ACin when the energy storage needs topping up, at night, and if manually triggered, and otherwise provide power from the storage on ACout to the power central.


TY

Multiplus-IIgridmultipluss iigrid meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
ejrossouw avatar image
ejrossouw answered ·

Given you will power all the loads from AC out, the inverter's metering can be used and no external meter is required.