question

Alex Pescaru avatar image
Alex Pescaru asked

Bug report: individual MPP operation mode reporting not working

Hi developers,

Multi RS Solar and Modbus TCP

MPP operation mode (general) 4543 reporting OK

MPP operation mode (individual) 4605, 4606 reporting NOT OK.

For example 4543 reporting 2 (MPP active) and in the same time 4605 and 4606 reporting both 0 (MPP off).

Alex


bug reportMulti RS
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @Alex Pescaru

What is Venus OS version?

Kind regards,

Thiemo van Engelen

0 Likes 0 ·
4 Answers
Thiemo van Engelen (Victron Energy staff) avatar image
Thiemo van Engelen (Victron Energy staff) answered ·

Hi @Alex Pescaru

In version 3.14, the MPP information per tracker is not available internally in Venus OS and then Modbus TCP returns 0.

Kind regards,

Thiemo van Engelen

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Pescaru avatar image Alex Pescaru commented ·

Hi developers,

Thank you for clarifying it for us.

Maybe on the "Document Versions" tab of the "CCGX-Modbus-TCP-register-list.xlsx" file, it worth mentioning, besides revision number, the minimum version of the Venus OS for those revisions to work.

Thanks again!

Alex


0 Likes 0 ·
Alex Pescaru avatar image Alex Pescaru commented ·

Hi @Thiemo van Engelen (Victron Energy staff) , @mvader (Victron Energy)

Kindly kindly please, can I ask you something?

On the future, can you please add one more state on DBus, for the "MPP Operation Mode" (/PV/x/MPPOperationMode), like "3=Scanning"?

In this way it will be easier on send_data() from vrmlogger, to handle the MPP scans and delay endpoint.send() during MPP scans, like you've done it on send_hourlydeltas()

Thank you!

Alex

0 Likes 0 ·
Alex Pescaru avatar image
Alex Pescaru answered ·

Now in 3.20 reporting OK.

Thank you!


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @Thiemo van Engelen (Victron Energy staff)

It's the last official/release version, 3.14

Alex

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @Thiemo van Engelen (Victron Energy staff)

And if we are still here, also:

2901, ESS Minimum SOC is always reading 100 (10%) no matter what you set in ESS setting page at Minumum SOC.

2903, ESS BatteryLife SoC limit (read only) also reading all the time 100 (10%), even if is set to "WITH BatteryLife)

2900 ESS BatteryLife reporting all the time 1

2902 ESS Mode reporting all the time 1, no matter what you set in ESS setting

Thank you

Alex

LE:

Now I see that those above are "com.victronenergy.setings", not "com.victronenergy.multi" and as Multi RS has a "hybrid" ESS, then they don't have how to show correctly.

Still, can be reported and set?

Thank you again!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Mutli RS Solar Datasheet

Mutli RS Manual