Running a 10kva Quattro with 4x Leoch Lfeli48-100TCAN batteries. can find any details relating to Quattr/Venus settings? Any ideas?
Running a 10kva Quattro with 4x Leoch Lfeli48-100TCAN batteries. can find any details relating to Quattr/Venus settings? Any ideas?
They are not officially supported, but the systems (Leoch lifepo4 not the exact unit you have) we have in the field are running 53.5v absorption and float 51.75v
You have 400AH of capacity.
In the manual use the value they call the equalizating voltage for absorption
Cut off 41V.
Just bus bar them individually to a bus bar like the lynx, as when you stack them, the charge current goes down for the pack. Check the specs in the manual.
It is stated quite clearly 100A for 1 but in Parellel it is 20A max. BTW information is also on a yellow sticker in front of the unit.