FLEET // USING VICTRON SKYLLA-TG 24VDC 50A BATTERY CHARGERS WITH LEAD ACID BATTERIES

Good day,


We as the ‘Pakoil Denizcilik AS’ are the technical ship management which has seven vessels. The 24VDC Distribution systems have been charged by Victron skylla-tg battery chargers in parallel on our good vessels. One was adjusted to the permanent boost-charge mode as the Main the other was adjusted to the equalize-charging mode via the dipswitches as the Emergency. You may find the related drawings below. Our good vessels are around thirteen years old and we replace the batteries every four years. We realized that the actual batteries are lead-acid type during the inspection. However, the Victron user guide warns that “do not permanently boost-charge sealed lead-acid batteries”. For this reason, we would like to have technical support from you about which mode should be set on the chargers to avoid an explosion of the batteries.


Could you please advise us which mode should be set on the chargers to be charged properly for the lead-acid batteries?


Thanks in advance for your invaluable assistance.


1644316881042.jpeg

1644316894192.jpeg

1644316907837.png1644316946037.png

Camel genuine 6-QWLZ-200 maintenance-free generator start lead-acid starter batteries with 12V200Ah

1644316976094.png1644316986634.jpeg

1644317111823.png



1644317017453.png

1644317028856.jpeg1644317042633.png

1644317064045.png1644317079773.png




support
1644316881042.jpeg (59.8 KiB)
1644316894192.jpeg (63.1 KiB)
1644316907837.png (174.7 KiB)
1644316946037.png (170.7 KiB)
1644316976094.png (270.0 KiB)
1644316986634.jpeg (24.8 KiB)
1644317017453.png (354.7 KiB)
1644317028856.jpeg (30.6 KiB)
1644317042633.png (252.0 KiB)
1644317064045.png (222.7 KiB)
1644317079773.png (303.7 KiB)
1644317111823.png (418.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

This is upto the person that controls the batteries - if they are gel or agm then equalizing is not needed and you would set both units to the same bulk and float levels - to do this turn on off do the adjustments - then do the other one with the first on turned off then your both back on -

when doing the adjustments one ONE is to be ON

anyway this is the way I would do it.