Easysolar 24/1600 switch all off panel, battery..

For the purpose of maintenance, do you disconnect the PV panels and battery connection by switching of the easysolar 24/1600 from the front panel or is this just to turn of the inverter and ac charger.

No line fuses or external breakers are used to minimize unexpected faults.

EasySolar All-in-One
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The switch is used to switch off the inverter charger. The switch does not affect the solar MPPT at all.
For maintainence purposes it's best to disconnect the PV array and the battery. Also disconnect any incoming AC sources to be safe.

2 comments
2 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

For the purpose of victron equipments do you disconnect battery+ then PV. There are conflecting theory.

Follow the manuals instructions.

Disconnections are in the reverse order.