Hi ,
Would anyone know why the SOC synchronisations are zero?
Hi ,
Would anyone know why the SOC synchronisations are zero?
Looks like a new system so how should there be some synchronizations counted?
A synchronization is counted after the SOC drops below 90% and goes up to 100% again.
thank you - I did not see that in the documentation about the SOC dropping below 90%
It is in the manual at chapter 5.5.
https://www.victronenergy.com/media/pg/SmartShunt/en/operation.html#UUID-fb41551c-8916-9f71-17bf-259a7fee2012
Additional resources still need to be added for this topic
28 People are following this question.