Lalith Gunawardena avatar image
Lalith Gunawardena asked
Can two 100A autotransformers be connected in parallel for a 200A split phase output?
Hi VE Experts,
Can two 100A autotransformers be connected in parallel for a 200A split phase output? The system will have two Quattro 15000 240V units. This is for a 240/120V, 50Hz system so we cannot use two 120V Quatto units in parallel as the 120V is only for 60Hz output.
Thanks,
Lalith
MultiPlus Quattro Inverter ChargerAutotransformersplit phase
Justin Cook avatar image
Justin Cook answered ·
Hi @lalith, welcome to the Community!
A 120V/60Hz unit can be programmed through VE.Config or VictronConnect to output 50Hz instead of 60Hz, so that would likely be your simplest solution - use 2 120V Quattros in parallel split-phase configuration (as you surmised) and programmed to output 50Hz instead of 60Hz.
Lalith Gunawardena avatar image Lalith Gunawardena commented ·
Hi Justin, thank you for the reply! Thanks for confirming the 120V/60Hz units can be programmed to output 50Hz. Do you know if there's a derate?
We were looking at using an Autotransformer as we wanted to use two Quattro 48/15000 units. However, the largest 120V is the 48/10000 so we may have to look at a different product as using 6 x 48/5000 units is a lot more expensive.
Thanks again.
satiagraha avatar image
satiagraha answered ·
I have the same question, however for different reasons. Can they be paralleled for 200A split phase (60Hz, US)? I just need the additional power and plan on two 15kW 240V units for the added power capacity.
30kW/240V= 125A, which exceeds the 100A rating of the autotransformer (even when the load is perfectly balanced)