Hi
Is there any way to disable unused GX Tank 140 inputs when connected to a CCGX only?
There is no 'Settings' > 'I/O' menu on the CCGX so I cannot use the method described in the manual.
Thanks
Gary
Hi
Is there any way to disable unused GX Tank 140 inputs when connected to a CCGX only?
There is no 'Settings' > 'I/O' menu on the CCGX so I cannot use the method described in the manual.
Thanks
Gary
Yes. These inputs show up in the analog inputs menu (Settings / I/O / Analog). There they can be enabled and disabled individually
Oh, yes, that is a bug.
The I/O menu appears only if analog or digital inputs are found, but the CCGX has neither.
The test for analog input is based on settings for the first INTERNAL analog input and does not look for the GX Tank 140!!!
If you have terminal access to your CCGX you can uncover the I/O menus with:
dbus -y com.victronenergy.settings /Settings AddSettings\ '%[{"path": "/AnalogInput/Resistive/1/Function2", "type":"int", "default":0} ]'
Thank you1
Root access documentation is available here: https://www.victronenergy.com/live/ccgx:root_access