vicky avatar image
vicky asked
MultiGrid and three ET112 at ACout1- how?
Changing my setup I'd like to connect three PV inverters to the ACout. So far had two ET112 to the ACout, which worked well. I.e. I don't see the individual PV values but the sum of both, which is OK as I work with the Modbus data mainly.
Today I tried to add a third ET112, so I changed the Bus ID with Gavazzi Software. The meter is recognized by the Venus, however - I cannot assign it to the ACout1 like the other meters.
It offers the tickboxes ACout1, ACout2 and ACin but If I tick ACout1, it defaults back to ACin.
Is there a limit of two meters at the ACout?
txs
PS: don't worry about the factor 1 rule, my three inverters never get peak power at the same time.
Energy Metermultigrid
Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·
Maybe @WKirby or @Izak (Victron Energy Staff) can help with this.
wkirby avatar image wkirby ♦♦ Warwick Bruce Chapman commented ·
Sorry, I don't know the answer to this one.
I can't test this because I only have two meters all together.
vicky avatar image vicky wkirby ♦♦ commented ·
Meanwhile I defined the third PV Inverter as a generator, where the VRM ID is 36 then.
I can read the power data via Modbus, however data is missing in the totals of VRM portal then. I'd appreciate if somebody could tell me f there is hope/an option existing to make it work as third PV Inverter at ACout. Maybe @Izak (Victron Energy Staff) ;o)
As a workaround I thought to cascade two meters. See picture. This would allow to capture all PV generated in VRM and I still would capture individual meters' data. Electrically it shouldn't problem, but I have no clue how the Venus/VRM uses and interprets the VRM IDs. Would my setup below work or screw up things?
Thanks guys
matthias-roetzer avatar image
matthias-roetzer answered ·
Hi @Vicky
Seems we are currently working on similar issues.
* How are your meters connected to your Venus? via native RS485 or via USB converter?
* Which Modbus IDs are you using 1,2,3,4 ?
I'm asking that because yesterday I tried to connect two et112 and one et340 to my venus (OctoGX) via ONE USB/RS485 converter.
* two devices are working with Modbus ID 1,2.
* all devices with ID from 3 and higher are not working together with Venus (but working well with UCS software)
In the community forum I found posts that only two meters in parallel are working and that further meters have to be added through further USB/RS485 converters
So I'm very curious how you successfully connected physically four of these meters to your Venus device.
I'm having a 3ph system consisting of three MP2. What I ran into further is that I don't know how to assign the ET112 PV Inverter measurement to the phase where each PV inverter is connected to. For digital feed in I have found the assignment, but not if PV inverter input is measured via ET112.
Your answer is highly appreciated.
Best regards,
Matthias
vicky avatar image
vicky answered ·
Hi @Matthias Roetzer,
I can confirm three meters using one USB/RS485 don't work with the Venus :o(. At least I was unable to make them work. They do work perfectly well with the CG software, even four meters work with CG at the same bus ..... So I ended up with using two RS485/USB Adapters where Meter IDs are 1 & 2 each bus. This is my current setup. (forget the Ethernet/Powerlan components, they are transparent for the RS485).
Screenshots for each meter's config from RConsole Energy Meters _Config.pdf
Hope this helps somehow.
1617630568812.pngAlthough the Console does only show one PV inverter at AC out (968W) it is the summary of all three ET112 meters.
matthias-roetzer avatar image matthias-roetzer commented ·
@Vicky Many Thanks! That helps a lot! Especially that Eth/RS485 is working well in you design.
Energy Meter Selection Guide