dewitpj avatar image
dewitpj asked
Getting WattHours from grid meter
Currently I can only see KwH from the grid meter (one of the ET112's). Even though uint32 counters are used, I can still only see 1/10th of a KwH. This document that I have says that the scale should be 100 (the modbus register sheet, version 2.20) - how can I enable this or get a wH value ?
Thanks !
Modbus TCPgrid
Hi @dewitpj, after rereading the list in excel, and its version in code [1], I think you can read up to 10Wh precision.
What are you seeing exactly? Always a 0 at the end?
[1] https://github.com/victronenergy/dbus_modbustcp/blob/master/attributes.csv
dewitpj avatar image dewitpj commented ·
That is correct, I only ever see the counter increase in 10's:
55720
55720
55720
55720
55720
55720
55710
55710
55710
55710
55710
55710
55700
55700
55700
55700
55700
55700
55690
55690
55690
55690
55690
55690
55690
That is the phase 1 from grid meter, top is latest. This is taken even minute with a +- 900w load on it.
It is worthwhile to note that I use address 2622 for these readings as they should contain a uint32 (all three phases in and out) - At the time I figured they might have higher resolution, appear not :)
Thanks !