steve-french avatar image
steve-french asked
Victron EasySolar configuration with small battery bank
Hi Folks,
I'm looking for advice on the configuration of a Victron EasySolar 3KVA system configured as grid-connected, zero-feed in ESS. I have eight 12v 100AH Hankook DC31MF leisure batteries configured as 4P2S giving me a 48v 200AH bank. The battery SOC seems sit around 95%, occasionally hitting 100% in the summer.
This has been running for a couple of years but I'm finding that most of the time the system seems to be cycling between a few minutes of Inverter On (discharging) until I see a "Low Battery" warning, followed by a few minutes of charging. The other "issue" I have is that whenever the mains power fails there seems to be insufficient battery power available to power the system - this results in an outage.
So, I have a couple of questions:
1. Is the battery capacity "sufficient" to use in this configuration and should it be able to perform as a UPS (albeit in a limited capacity) when mains power fails?
2. Is the discharge/charge cycling to be expected - looking at the system now I have 120W AC load and its cycling every few minutes...?
3. In the absence of any specific data for these batteries, I have them configured as Gel/AGM as this seems to match the only data I manged to get from the manufacturer:
Manufacturers Recommended Battery Voltages
Daily Cycle: 14.4 (57.6)
Float: 13.2 (52.8)
EQ: 15.5 (62)
My Configuration (Note: Float is a little higher than manufacturer recommended):
Dynamic Cutoff is also at the default for Gel/AGM - is this ok?
Restart Offset:again default for Gel/AGM is this ok?
Any help/advice gratefully accepted!!
EasySolar All-in-One
dazey77 avatar image
dazey77 answered ·
I think you mean your bank is 4S2P (two parallel circuits of 4x12v in series, so effectivly 2 x 48v in parallel and the 200AH you say)
I would suggest you check each battery and see if one has failed.
steve-french avatar image steve-french commented ·
Yes, you are correct they are configured as 4S2P (I thought that but typed the opposite - doh!)
Does the behavior indicate a failed battery - ie: should it be able to work with a relatively small (and leisure type) battery bank?
dazey77 answered ·
It depends a little on the loads. If its only lasting a few mins and the system is actually pulling 3kw, then its probably performing correctly. If your only pulling a few watts and its lasting a few mins, then its probably got an issue!
if I understand right and your only pulling 120w for a few mins then something is not right. The batterys should be able to support that level of load for a long time.
marekp avatar image
marekp answered ·
This info suggests that your battery is toasted.
Check voltage of each battery individually during charging and discharging.
Do you have battery balansers?