Shore power problem

Having a problem connecting shore power. I have a multiplus 3000 120 16 together with 100/30 and 100/50 smart mppt with a Cerbo gx. When I connect the ac in it throws the main beaker on the dock. Tried not connecting the earth...same. If I disconnect the ac out all works good and charges my batteries. Now the weird bit. With the shore power disconnected the inverter powers the whole boat without a problem. Any ideas?

shorepower
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

"main beaker on the dock"


What type is that? MCB? RCBO?

0 Likes 0 ·
iandou avatar image iandou seb71 commented ·

Pretty sure it’s a MCB

0 Likes 0 ·
seb71 avatar image seb71 iandou commented ·

Then it's not an residual current issue.


It's either a short or overcurrent.

0 Likes 0 ·
1 Answer
Paul B avatar image
Paul B answered ·

Best guees is that the dock has its Active and neutral connection the wrong way around or the cord to the boat does


try reversing the two connections in your cord the brown and blue or in the USA black and white


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

I would check if the Line and Neutral are correct. Not just reverse them and see what happens.