rohikeo avatar image
rohikeo asked
Is there a power limit between Loads and Critical Loads for Multiplus II?
Hello Community, I could not find any information regarding the following question: If running a PV inverter on critical loads output of a MultiPlus II to supply regular loads during grid failure, is there a power limit to regard? Would a 5kVA MultiPlus II unit be sufficient to connect a 10kVP PV system on Critical Loads output? Thank you!
Multiplus-IIMultiPlus Quattro Inverter Charger
Rob Duthie avatar image
Rob Duthie answered ·
Hi
No, 1 to 1 rule applies here.
Regards
Rob D
NZ
rohikeo answered ·
Thank you Rob, I reckon the "no" answers my first question. Take care!
Rob Duthie avatar image Rob Duthie commented ·
Hi
That,s OK, yes use AC coupling to use a over sized PV system etc.
Regards
Rob D
NZ
rohikeo answered ·
Just to clarify it if anyone will read this question in the future:
Using a PV inverter on the protected output of a Multiplus will require a 1:1 sizing of both units. A more cost efficient alternative could be an AC/DC coupling like shown here: