SIMPBMS and Tesla batteries

Hi Folks. I'm looking for some support or guidance from the brains trust. I am using 8 Tesla Model S battery Modules with a SIMPBMS in a 48V system. The SIMPBMS is connected via CANBus to an EasySolar II (Multiplus II GX effectively). I'm using an ESS Assistant and DVCC. It all works well, other than the depth of discharge. The Multiplus reports Low Battery on L1 and starts drawing from the grid once the battery voltage falls to ~40.6V, or 33% SOC (6S battery). The firmware is all current and shouldn't have the old limitations. I can't see how to draw deeper in the battery. Please note, this isn't shouldn't be inverter start/stop issue with the known limitation of inverter restart voltage as the load on the inverter is constant.

Thanks

MultiPlus Quattro Inverter Chargerlow battery warning
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
stxShadow avatar image
stxShadow answered ·

There is no possibilty to change this. It is firmware related in the Multiplus. 40.6 Volts is btw in a 12s System. The energy you would get below this point is marginal as the voltage drops rapidly -> see attached graph. In Terms of service life you should even not go deeper. The packs will last a lot longer if they are not discarged to deep and not charged over 49.2 Volts.

Jens