bigbloke avatar image
dimension question - 75/15 versus 100/20 - max PV input ?
Hi All,
* Charging 12 volt 220AH (2 x 110AH battery bank)
* 2 panels both 24V short circuit - already purchased
* Planning to install in series , looking to select a controller
75/15 or 100/20 ?
Well...
My PV voltage is well under 75 at 48V peak
My PV current will be about 6A
So on paper the 75/15 firs the bill
BUT - my total "theoretical" panel power in Watts will exceed the "nominal" figures quoted here:
https://www.victronenergy.com/upload/documents/Datasheet-SmartSolar-charge-controller-MPPT-75-10,-75-15,-100-15,-100-20,-100-20_48V-EN.pdf
by a good few watts
given I and V are well under, is that alone enough to say "the 75/15 will be enough"?
or should I err on the side of caution and get the bigger one please (and why please)
Many thanks in advance
Regards
BB
MPPT - Solar Charge Controllersmart solar set-up help
Do you have a datasheet or a model number of the panels for us?
The important specs are the open circuit voltage Voc + temperature compensation (%/°C) and the lowest temperature at your place.
You can enter all specs into this calculator:
https://www.victronenergy.com/mppt-calculator
Share
N-DEE avatar image
If you're using them in surroundings with higher temperature i would take the 100/20
They "only" have 100% up to 40 degree. 75/15 may go well beyond 40 degree resulting in e.g. 80% of 440w (-> 352w) @24v
br,
Andy
Share