nicetrip avatar image
nicetrip asked
Multiplus - AC-1 AC-2 switch over for Aircon start on genset
Hi, I have a Multiplus in a motor home. All AC was connected to AC-1. Problem was, if somebody pulls the power lead or the generator runs out of fuel in the night, the Multiplus switches to battery and might discharge them too much. AC-2 drops the load in that case, but because its to sensitive, I can't use it to start the AC on the 'at start' unnoticable fluctuating generator.
Its a nearly new Honda EU2000i, perfect for the load.
So I installed an external switch that lets me switch the AC load from AC-1 to AC-2 after a few minutes, ones the generator is running acceptable for AC-2.
I am about to extend the switch with adequate cables to the inside.
Question: Is that a known problem and does it has a solution already?
Is there a config setting I can change?
ac out 2
Hi @NiceTrip
There are lots of ways to 'slow down' AC 2 connecting, but there might be other options also:
-what settings do you use with the generator? as it is an inverter type 'variable speed' generator, do you have 'Dynamic Current Limiter' enabled?
nicetrip answered ·
Hi Daniël, thanks for the very quick reply!
I did a firmware upgrade to 2609474 first.
I tried the 'Current Limiter' enabled'' but with no change. AC-2 drops the load just when the air con adds the compressor to the fan. Fan until then it holds.
settings :
General - 16 A input current, battery monitor on with 500Ah,
Inverter - default
Charger - enabled, weak AC, 14,4 13,7 100A rest default
Virtual sw - default
I have the remote bridge on the board extended to a switch inside the camper, so its overriding the inverter+charger ON switch position.
Could I try some more?
Cheers
Chris
Hi @NiceTrip
if you want to increase the AC2 connection time, use assistants for a custom time setting.
you could try this:
nicetrip answered ·
Perfect Daniel!!!
That worked out well, aircon currently running on AC-2. I wouldn't be a problem to add more seconds ... like take 300, that would give the generator some time to warm up, and the air con will run fan only for a minute before adding the compressor?
Great versatility! One more question. I will extend the bridge port on the board to switch the Multi on and off remotely. What voltage is on that port against mass? I would like to run a small LED on that switch.
thanks
nicetrip answered ·
Hi Daniel, me again, sorry :0)
I noticed now that ACOut 2 doesn't use the battery at all? Good would be a combination of inverter on battery until AC1 becomes available, then use AC1 (generator or shore power), like default on ACOut 1.
I use the espresso machine on inverter/battery every morning.
How about -> when then AC1 becomes unavailable 'drop ACOUT 1'. After restart of the Multi it starts again on battery.
Is that possible? Otherwise after a quite morning with coffee I still have to switch to ACOut 2 to start the air con on generator, when it gets warm over the day.
Pantelis Zirinis avatar image
Pantelis Zirinis answered ·
I am having the same issue on a Northern Lights 5kW generator. Before installing the inverter the generator could take the load from both units without any issues.
On AC2 when the air con starts, AC2 dies. If I try it on AC1 it works fine.
I will try with the dynamic setting tomorrow and see how it goes.
I have a feeling ac2 is sensitive to voltage drops and for some reason feels there is no generator running, as it becomes available again in 2 minutes.
I am using a Multiplus 3000/12/50