Easysolar 48/5000/70-100 new install. System ran fine for 7hrs but now inverter is turning on/off every few seconds. No faults are shown and battery voltage is 55volts. All loads from inverter have been isolated.
Please
Help
Please
Help
Please supply more information
1, whats connected to the multiplus ie ccgx or gx unit
2. what are all the settings screen shots would help
3. what firmware version is the multiplus on
4. is it connected to a vrm
5. a wring diagram of the setup would also help
Hi Paul,
All inverter settings are at default, connected is the colour controller that comes standard with the easy solar inverter.
I am running 48 volt 280ah agm batteries with 3.9kw of solar power.
I have run a firmware update check through the colour controller and it says it has the latest update.
At this stage there is no permanent internet available to connect to VRM.
I have noticed that none of the charge lights, bulk,float ect. Are on unless running off generator. The colour controller shows batteries charging on pv.
Hi @Rumcity
This sounds suspiciously like 'AES/Search Mode' has been enabled. That wouldn't normally be the case by default, but who knows?
I don't think the GX can tell you this, nor dipswitches on that model. You'd need VEConfigure via VRM, or locally with a MK3 adaptor with preloaded lappy.
If that were the case, the inverter should fire up with a load on anyway, but mightn't suit tiny loads. It's described briefly in the manual:
Thank you for your reply. Inverter seems to turn on/off whether I have load or not. If I turn all power off to easy solar for a period of time. It works for a period of time 1hr-2 hrs but then randomly starts turning inverter on/off float light flicks on for a split second then off. I have tried this with only batteries on, pv off and both on same result.
17 People are following this question.