i plan to install an EasySolar II GX (1-phase) with PV panels and batteries in a house connected to 3-phase grid.
Here in Germany the official gris meter uses balanced metering (if I use high current on phase 1 but feed back the same on phase 2, the meter is not counting).
Thats why I would like to connect a 3-phase grid meter (EM24?) in order to measure the total load on all 3 phases.
The EasySolar should then optimize self consumption by using the total load on all 3 phases, even though in reality it is feeding only on phase 1.
Example:
House draws 5A on each phase 2 and 3.
Easysolar should then feed back 10A on phase 1 in order to optimize self consumption.
Is that possible and which settings do i need to configure?
Best regards
David
EasySolar All-in-One
rainerb avatar image
rainerb answered ·
Hello David,
If your system is controlled by a GX device with grid meter and ESS assistant in the Multi, then you can activate the "phase compensation" function. This is what you want to achieve according your post. I have such a system configuration and it works quite well.
I would also recommend to read the ESS design manual (phase compensation is chapter 7)...
https://www.victronenergy.com/live/ess:design-installation-manual
Regards
Rainer
shelldor answered ·
Hi Rainer,
thats what I was looking for! Thanks a lot for your help!
Regards