My ESS system build with ccgx ,3x quarto 48/10000, 3750ah lead acid battery's is not showing battery % on ccgx is this only possible with an bmv.
Use Ve Configure 3 with an MK3 and enable Battery Monitor on the first tab.
What type of batteries?
Did you type correctly 3750Ah of batteries ? How is that made up?
Wow! That's a lot of power.
What is taking care of balancing the component batteries in each 48V unit?
By the look of the Venus screen, you have "Has DC System" enabled but you do not have a BMV in place to allow you to measure that.
Do you have DC loads other the the Multiplus on the batteries? If no, then disable "Has DC System".