Hi Guys

Received 2 x CCGX units. Fitted 1 to a system. Unit started with Victron Energy logo & then showed "starting" below logo as usual. Next unit went to Victron logo but does not show "starting". Stays with logo for 20 minutes.

I have tried resetting & disconnecting power but will not go the start.

Any thoughts please.

Thanks

Dino

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Bring it back to your dealer and get a new one.

Maybe you can try to make a manual firmware update:
https://www.victronenergy.com/live/ccgx:firmware_upgrade_to_v2
But I would suggest to exchange the faulty device.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Please make sure that nothing is connected at all to the CCGX except for the power (and that it is a sufficient voltage and current supply).

I have had CCGX units stuck on a boot loop from damage to the USB extension cable (even with no device/accessory connected).