I have installe new CCGX on a installation. When I turn the system on it does not shows any AC load values, only the critical loads value. What is the reason for this?

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mark avatar image
Mark answered ·

If your system is setup as an ESS 'Energy Storage System' it is normal for all loads connected to the MultiPlus output to be treated/shown as 'Critical Loads' as they will remain powered by the inverter/battery if AC Input is disconnected.

With a grid meter connected, any loads connected directly to the AC Input side will be treated/shown as regular 'AC Loads' since they will be disconnected in event of a grid failure.

https://www.victronenergy.com/live/ess:design-installation-manual