tony-towers avatar image
tony-towers asked
Can I control AC OUT 2 if AC IN is available?
I use the following assistants:
If no AC Input available, the logic works well. However, if there is AC Input 1 or 2, the AC Out 2 is active (voltage on) after some minutes whether or not AUX2 is open or closed.
I can hear the internal relay opening or closing following the logic above but the AC OUT 2 remains active.
Therefore, it seems there is an internal logic which allows voltage on AC OUT2 if ACIN 1 or 2 are available after some minutes.
I use a system with Quattro 48/5000/70-100/100 120V.
Manual says this behaviour is normal so I wonder if controlling the relay of ACOUT2 only works when no ACIN is available, so in that case, ACOUT2 IS ALWAYS AVAILABLE AFTER 2 MINUTES IF AC IN IS AVAILABLE.
Can anyone confirm this to me, please?
Thanks in advance.
ac out 2
tony-towers answered ·
The problem is that on a system with multiple inverters such as a three phase or single phase with more than one inverter, you have to add assistants on every single inverter to control ac out 2, otherwise it doesn´t work.
multiphase: yes
parallel units: it depends, ac-out is controlled from the master, so only in the master.
as soon as you use the AC-out2 in an assistant, the standard behavior is turned off.