question

Vicky avatar image

How to connect ET340 to Venus via ETHERNET ?

I am stuck with my ET340 setup .
ET340 is sitting in the power distribution cabinet (solid steel case - forget WIFI ).
The pipes, laid in concrete, I had forseeen for additional wires, have been wrecked by the builders - squeezed...
So I end up having no option to -route an additional wire to my Venus/ Multigrid, two rooms away.

I do have Ethernet LAN in the cabinet and I am aware of RS485 <-> Ethernet adapters, but will the Venus / Multigrid be able to communicate ?

rs485
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
Vicky avatar image
Vicky answered ·

Txs, Zigbee was the first choice, but wireless won't work sitting in a rock solid steel cabinet :(.

I ordered two simple RS485-Ethernet adapters right now, will give it a try and report back

2 comments Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks, it would be great to have some feedback!

Hi Vicky,

You can use the Ethernet cable as an extension of the Rs485 cable!, ie..a twisted pair for the ground a twisted pair for each of the data +/- of the inside of the Ethernet cable.I have used this in the past with no issues,no adaptors are used so no problems encountered!

Vicky avatar image
Vicky answered ·

To finally having three energy meters working, this is how I had to set it up at the end. Three meters at one bus didn't work. See here



Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vicky avatar image
Vicky answered ·

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image
Mark answered ·

Pretty cool set up there Vicky!

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vicky avatar image
Vicky answered ·

... after a couple of hours, taking hurdle by hurdle I made my setup working.

Now ET340 meter is connected by quite a chain of components.

ET340 Meter -> RS485/Ethernet Converter -> Ethernet/Powerlan -- >Powerlan/Ethernet - > Ethernet/RS485 Converter- >RS485/USB cable -> Venus GX

Additional cost beyond the USB cable you need anyway:
2 pc. RS485/Ethernet converters € 53.-
Devolo Powerline for the distribution cabinet €150.-
AVM546E €50.-

So not a steal, but helps big time.

I might write up the setup later, or on demand if this of interest for somebody.




1 comment Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

That is awesome Vicky!
Thanks or sharing and letting us know that it works. Please keep us updated its reliability.

Vicky avatar image
Vicky answered ·

Thanks Mark, I understand what you mean, but I don't have Ethernet cabling in the cabinet. I have Ethernet made available over Powerline. So I'll try to connect RS485-Ethernet-Powerline-Powerline- Ethernet RS485 :o) No the most simple and cheap way, compared to a stupid pipe with cable..., but the only one I can see here as an option. I'll let you know how it worked out at the end

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

WKirby avatar image
WKirby answered ·

Those sort of adapter / converter gadgets are not supported by Victron.
That's not to say that they won't work, it's just that if you do decide to try them, you'll be on your own.

Have you thought about using a wireless Zigbee connection?

https://www.victronenergy.com/live/energy-meters:et340