question

Martin Coetzee avatar image
Martin Coetzee asked

et340 to monitor clients other phases on 3 phase install with single phase ess system

My client wants to monitor hes other 2 phases in a 3 phase installation that has a 10 Kva 1 phase system in hes 1 phase carrying most of the house.

if i replace the et 112 with a et340 will he be able to see each phase separately and not as one reading. will the ESS system stil work on the 1 phase without problems ?

He wants the monitor it remotely on the VRM portal and compare records with the utility provider.

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Murray van Graan avatar image
Murray van Graan answered ·

Hi Martin, yes that will work. In the remote console you will have live data of each phase, and in advanced tab you’ll be able to see the power consumed from the grid, per phase. In the dashboard, the consumption figures would be totals for all three phases together. In order for this to work, the phase feeding the ESS system will need to be L1 of the ET340 - not on L2 or L3.