CCGX Controlled export limiting

Is there a way to set an export limit to the grid using the CCGX unit or do i require external metering?
I know the fronius zero export will stop all export to the grid but is there a way i can set a specific value for how much is exported?

Curious of this for both applications when AC coupled inverter is on either the input or output of the multiplus.

MK3
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Not officially, or as part of the interface. As you have said zero export is possible, as is full export.

There is no option for limited or partial export, except setting a limit to the AC input current limit, or Invert power limit, for DC solar. Both of these “workarounds” have other issues and implications.

Technically something may be possible using the ESS mode 3, or NodeRed tools - but these are not thoroughly documented.

1 comment Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

No worries, cheers mate, will just use a fronius energy meter.