gagan-ranatunga avatar image
gagan-ranatunga asked
Victron Quattro 15kw high Voltage Alarm and Internal Failure
Hi
I have installed a victron 15kw quattro with 6x us3000C pylontech batteries and when it goes to 100% it gives out a high voltage alarm and internal failure error and trips the whole system. Please let me know how to fix this I have tried everything
MultiPlus Quattro Inverter ChargerPylontech
The alarm is coming from the battery monitor (should be the Pylontech) not from the Quattro.
Under advanced you can enable diagrams for the battery voltage/current, min/max cell voltage and charge/discharge limits from the battery.
If it is the very first time charging to 100% you should do that with a small current to give the battery time to balance the cells.
Did you install the system according to the instructions?:
https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom
gagan-ranatunga answered ·
HI Mathias,
Yes I followed all the instructions, but it is still pumping up the voltage to 53V which shuts down the battery bms and cause the victron to shut down, I have limited the voltage to 52v on DVCC and tried doing it on VECONFIG aswell but no Luck, any comment on how to fix this?