Venus GX and Modbus

Hi all,


I'm trying to use Venus GX to communicate with my Siemens PLC. At Venus GX I am using VE. Direct 1 and VE. Direct 2. At Siemens' TIA PORTAL, we established the Data type, Start Address and UNIT. However, I couldn't establish the connection. So I used a Modbus Scanner to see if I was really getting the information from Venus yet I can't access any modbus messages from the device. I used the data as Holding Register, I have already activated the Modbus function of the device and I don't know what is missing.


Thank you in advance

Venus GX - VGXModbus TCP
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
WKirby avatar image
WKirby answered ·

MODBUS messages are not sent on the VE.Direct (serial) interfaces.
The MODBUS messages are MODBUS-TCP messages sent on the LAN.