question

inhabor avatar image
inhabor asked

Honda EU 3000, can someone please post detailed instructions of how to wire the CCGX to my generator?

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Hi. This is a hard call. You'll likely need an aftermarket '2-wire' remote module added to the Honda, and it's really beyond Victron control. Perhaps your local Honda man or generator supplier?

At the CCGX end the 'Relay' terminals are the ones to use for the '2-wire' source.

https://www.victronenergy.com/live/ccgx:generator_start_stop

Maybe you already have a module, or perhaps someone here can recommend one.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

Hi @JohnC, the CCGX only has one set of relay terminals (not NO & NC) and it is currently not possible to invert the 'generator start/stop' relay function.

There is an option to invert the relay but it only relates to the 'alarm' function.

It would be good to add in this functionality (to invert the gen start/stop relay) as it is helpful with using the 'generator start/stop' function as a simple dump load controller, where the logic needs to be reversed.

0 Likes 0 ·
JohnC avatar image JohnC ♦ Mark ♦♦ commented ·

Ok, the CCGX manual doesn't seem to clarify that, but I'll believe you. And edit that piece out..

0 Likes 0 ·