n-dee avatar image
n-dee asked
SOC Limit
In the actual Firmware release the SOC limit will be exceeded by 5%
Afterwards the inverter kick in to load the missing 5%
Is this issue already known?
SOC
@N-DEE
You are probably going to have to explain a bit more about your set up?
Firmware? Components? Peaks shaving allowed under mon SOC? Where is the generator set to start up?
n-dee avatar image n-dee Alexandra ♦ commented ·
Well ok, little bit mor details :-)
Cerbo Firmware 3.14, no generator, standardequipment (3x Multiplus II 5000, 2x SmartSolar MPPT RS 450/100)
ESS optimized without batterylife - SOC 25% - Peakshaving always allowed.
n-dee avatar image
n-dee answered ·
Tried some settings and found out that this occours only with "peak shaving always"
On peak shaving above minimum SOC only everything is fine.
Don't know if thats the way it should work though...