question

David Gould avatar image
David Gould asked

CCGX relay for generator

Can I reverse the relay login on a CCGX? My generator needs open cct to switch on

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Paul B avatar image
Paul B answered ·

You would need to attached another relay to it to achieve the reversing option ie a NC/NO relay

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image
wkirby answered ·

There is no option to reverse the relay logic for a generator.
You'll need to use the relay output to drive another relay with NC contacts so that the circuit will open when the internal relay contacts close.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

David Gould avatar image
David Gould answered ·

Thanks, thought that was the case but was worth asking