valvetdk avatar image
valvetdk asked
is the calculator wrong, or something i dont know?
Am I mistaken, or is the calculator wrong?
I used the calculator to determine the size of my MPPT. My solar panels have the following specifications, and I used two units of this model in the calculation, resulting in an indicated MPPT of 100/30 for my 24V system:
  • Pmax = 405
  • Open circuit voltage (Voc/V) = 37.15
  • Short Circuit current (Isc/A) = 13.78
  • Vmp = 31.18
  • Imp/A = 12.99
I connected both panels in series, so the formula for my voltage is 37.15 + 37.15 = 74.3, and the current remains the same at 13.78 A. However, when I use the calculator again and input that I want to connect 2 strings in parallel, the calculator suggests upgrading to an MPPT 100/50 model.
But why? Doesn't the voltage remain the same, 74.3 Volt , and the current becomes 13.78 + 13.78 = 27.56 A? Shouldn't I still be able to use my MPPT 100/30 with 2 series + 2 strings, or why does the calculator recommend upgrading to 100/50?"
Solar Panelmppt calculator
klim8skeptic avatar image
klim8skeptic answered ·
@ValvetDK Shouldn't I still be able to use my MPPT 100/30 with 2 series + 2 strings, or why does the calculator recommend upgrading to 100/50?"
It comes down to the array power and mppt output current at battery voltage.
The 100-30 can handle an array of about 880w, with its output current of 30a into a 24v battery. 2 of your panels is 810w, a good fit for the 100-30.
The 100-50 can handle an array of about 1400w, with its output current of 50a into a 24v battery. 4 of your panels is 1620w, a good fit for the 100-50.
valvetdk avatar image valvetdk commented ·
Oh, so it's not enough to just look at the maximum voltage and current an MPPT can handle; one also needs to take wattage into account, right?
klim8skeptic avatar image klim8skeptic ♦ valvetdk commented ·
@ValvetDK Yes. You dont want to hook up an 1620w array, and only get 880w out of your 100-30 mppt, into your battery.
prein avatar image
prein answered ·
Yes, the 30 amps is not only on the mppt side, but also on the battery side.
That means that with 24V battery you can only charge with 30A= (*24=720 watts)
Nothing breaks when you do connect them, because you stay within spec. But there is much solar energy unharvested