Eesysolar remote configure/disable ac backup

Dear All,


I have the following situation. On the location far away from me, i have installed Victron Easysolar 24/1600 with 810 Wp PV modules, 2 x Victron Gel battery 165 Ah and Venus GX communication.

Since on the system AC power is available as well, i have set it to work as a backup with following configuration:

-ignore AC input

-do not ignore AC input, when battery SOC is below 40%

On the first day, system was working autonomously

Second day, battery voltage was going up, but inverter was reading SOC as going down and started AC source. Since then, it is working purely on AC supply and is ignoring PV modules. My main question is:

How can i configure it remotely to use AC only as a backup and not as a primary source?

I also want to point out that i did not install VE direct cable, as there was no clear instructions i need it, Venus is connected to easysolar only via ethernet cable.

BR,


Rajko




EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Rajko

The ve.direct cable is needed, otherwise the Venus doesn't know the system is being charged by the MPPT, and only counts what is used by the inverter, thus SOC going down.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rajko avatar image rajko commented ·

Dear Daniël,


Thank you for your reply. It makes sense now, just that i was not aware of that before. Can you reply to my main question, can i disable ac charging remotely?


As a side question, are there plans to connect communication between the charger and inverter internally? It would be much easier without needing extra cable.


BR,

Rajko

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ rajko commented ·

Hi @Rajko

they cannot be connected internally, as they are different protocols (VE.bus and VE.direct)
On the bigger models there is a Color Control GX build in, that is already connected to both the inverter and the MPPT.

You can remotely configure the Multi, for now I'd change the SOC based AC-ignore into voltage based.

https://www.victronenergy.com/live/vrm_portal:remote-veconfigure

0 Likes 0 ·
rajko avatar image rajko Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Dear Daniel,

This looks very promising to solve my case. While you are replying so fast, i will also need quick info, which voltage does corresponds to 40% SOC. I cannot find this data on the datasheet.

BR,


Rajko

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ rajko commented ·

SOC vs Voltage: depends on a lot of factors...

to save on you batteries, I'd first try 24,5V connect to grid, 25,5 disconnect.

0 Likes 0 ·