Rasmus Mikkelsen avatar image
Rasmus Mikkelsen asked
Wire size when doubling battery capacity
Hi all
I have a question I'm thinking about.
Currently I have a 14s200p 18650 li-ion 20kwh of storage working really good. With multiplus 2 48/5000, 6.2kwp solar panels with 250/100mppt.
I'm in the process of doubling my battery capacity so I will have 2 banks of 14s200p.
I'm currently using 70mm2 cable from battery to main breaker to victron distributor, and from there to MP2 aswell.
Please see the drawing I made.
I know the manual states 70mm2, but wondering since the current draw from each bank will be half, if I can double down on wire size to 35mm2?
#1 On the picture is current setup
#2 Is what I'm thinking about doing.
I have never experienced dc ripples, but I'd like to avoid that, thats why im asking :-)
Thank you
Regards Rasmus
Multiplus-IIESSLithium Batterybattery connection
jetlag avatar image
jetlag answered ·
A 35mm² cable is absolutly fine for ~42A per bank. In theory you could even go down to 10mm² for each bank.
The 70mm² between the distributor and breaker and Multiplus2 is also way oversized. It may depend on the cable length, but I quess it is not more then 2m.... So with that proposed sizes you are absolutly fine.
Rasmus Mikkelsen avatar image Rasmus Mikkelsen commented ·
Thank you, yea I just worry about dc ripple I have heard so much about, that's why I used 70mm2. I think I have more than 2m, probably 3-4m iirc :-)
kevgermany avatar image
kevgermany answered ·
Try to keep the cable lengths the same to each bank. Although your cables may be larger than needed, better to do this and avoid a rewire when you install a larger consumer.
Michelle Konzack avatar image
Michelle Konzack answered ·
Because i am courious:
Is the 14s200p a DIY project?
If yes, how long did it take you to solder 2800 cells together?
Hi yes from dead e-bikes. Well it takes a bit of time, I'm not soldering I'm spot welding with fuse wire.
Generally a big project testing all those cells, and im only using cells that test within 15% degradation. Meaning I have to type in every cell in a spread sheet and compare capacity to when they were new.20230924-130728.jpg
Also when you have some sort of OCD it takes even longer :-)
2 Likes 2 ·
Michelle Konzack avatar image Michelle Konzack Rasmus Mikkelsen commented ·
Wow, you are realy crazzy, but not alone. On Youtube I found many others too...
Have fun and nice day
giorgos avatar image
giorgos answered ·
it is important for the cables to the batteries to have the same resistance whatsapp-image-2023-09-28-at-223619.jpg
Thanks, yes from each battery pole to victron dist. I will make sure will be exactly equal lenghts.