Venus OS v2.32~3 available for testing

Dear all,

Just now, we released beta version v2.32~3 for testing. See below for the changes.

For information on how to join, or leave, the Venus OS beta testing program, as well as other information about it, see this document.

In case you see any issues or bugs, please post below as an answer or comment. Thank you!

Only one change compared to v2.32~3


  • Minor improvements; all related to production in the factory.


The results of v2.32~2 are good: it solved below described communication related system shutdowns on all systems.

v2.32 will be available and announced as an official release within a few days.

Best regards, Matthijs


Ps: changes and information of the previous v2.32 beta versions:


  • Fix CCGX causing VE.Bus communication errors, such as Error 17. Also it can cause a false Error 24, which is normally not related to communication. To be affected by this issue, the system must have a CCGX, with part number BPP010300100R. Also recognisable by the country of origin: Hungary. All other CCGX part numbers, made in China and India, are not affected.

    We started shipping the affected model in 2017. And since early 2019 we're only shipping the affected units: by that time there was no more stock of the older units in any of our warehouses. The CCGX as used in some EasySolar models is not affected.

    The issue was that that version CCGX transmitted on the VE.Bus network even when it should not. Causing collisions, ie. errors in the communication. More units in a system (three phase, and then especially with parallel units also) means that its more sensitive to this issue. Single system units are very unlikely to be affected by it; I've not yet seen that once.

    Thank you to all people that have reported and helped to fix this.
  • Fix the System Setup -> DVCC -> Charge current setting not working, if the Venus booted while there is no PV on systems with normal batteries. Systems with intelligent can-bus connected batteries are not affected by the bug. Thank you @John Hagtharp for all your effort in getting this fixed. This issue was introduced in v2.30
  • Fix the ModbusTCP register for the PV Inverter serial number(s) no longer working. The recently introduced 32-bit energy registers for PV-inverters overlapped with the serial number registers. This is fixed by moving the new energy registers from 1040 to 1046. The issue was introduced in v2.31.


Should you now go and install the v2.32~2, which is a beta version, on all CCGX systems you installed recently, to prevent Error 17 and other issues? No.

I recommend to do that only for systems that have issues. For systems not having issues, I strongly recommend to wait until this version is made available officially. As always, beta versions are not at all intended to run on production systems.

If you do choose to install this beta version, make sure to set the system back to update to official releases. Don’t leave it configured to auto-update to beta software.

Venus OS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
alexandra avatar image
alexandra answered ·

Hello Matthijs,

in 2.32-2 and 2.32-3 I have experienced that the function of the Phase compensation is inverted.

When switch off, the phases are compensated, when switched on there is no compensation.

(Color GX with a 3 Phase Multiplus 5000/48 System)

Thanks a lot

Alexandra

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Hi Alexendra as discussed last night over email, this is likely a misunderstanding due to the rather multi-interpretable term 'phase compensation'.

To see what the setting does when its on/off, read this chapter in the ESS Manual:
https://www.victronenergy.com/live/ess:design-installation-manual#phase_compensation_-_further_information

0 Likes 0 ·
mka avatar image
mka answered ·

Thank you for the revew.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

FYI: v2.32 was released officially earlier today

https://www.victronenergy.com/blog/2019/07/02/venus-os-v2-32-various-fixes/

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gndubi avatar image gndubi commented ·

Hello @mvader (Victron Energy Staff), After updating the firmware of the inverters and CCGX to the latest firware (460 and 2.32 respectively), it's impossible to read the remote VE Config file. We are basically getting the below error on opening the file.

0 Likes 0 ·
config-error.png (288.6 KiB)
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ gndubi commented ·

Hi, you probably need v2.33 Venus OS.

0 Likes 0 ·
gndubi avatar image gndubi mvader (Victron Energy) ♦♦ commented ·
@mvader (Victron Energy Staff) Could you kindly share a link to v2.33. This is not saved on the Victron Professional website. Our preference would be to upload via SD Card due to very poor connectivity at site.

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ gndubi commented ·

Hi @Gndubi, oh yes, I’m sorry! I must have missed updating those files on vicprof

We’ll fix that tomorrow, in the interim, you can also download them via the links here:

https://www.victronenergy.com/live/ccgx:firmware_updating


0 Likes 0 ·
Ben Graham van der Sandt avatar image
Ben Graham van der Sandt answered ·

Picked up an issue with a recent Quattro ESS system with BYD lithium batteries.

after updating to 2.32 ccgx gave Alarm "Hardware problem detected #42 storage is corrupt on this device"

reverted back to 2.18 and system ran fine, no issues.

once it updates to 2.32, it gives same error on reboot.

left it on don't update manually for the interim



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Hi @Ben Graham van der Sandt, #42 means the unit needs to be serviced. v2.18 doesnt recognise the problem, but it will still be there; just unseen.

It means it will not remember, or not always remember, any settings you make.

Best to do is contact your dealer.

0 Likes 0 ·