adamr100 avatar image
adamr100 asked
Tank GX Reading Always 1v
Hello. I have a tank GX plugged into my RPi based set up. I have this sensor: Longzhuo Liquid Level Transmitter, TL-136 Liquid Level Transmitter Water Level Sensor Detector 12-32VDC 4-20mA Signal Output for Precision Measuring(1/2/3/4/5M)(0-2M) https://amzn.eu/d/6hyLNjz
The signal from the tank reads 1v continuously no matter how full or empty the tank is
What am I doing wrong? Thank you
tank monitor
derrick thomas avatar image
derrick thomas answered ·
In the settings menu for the tank sensor have you selected "current" for the sensor type?
adamr100 avatar image adamr100 commented ·
It was voltage I’ve just changed to current and it’s 0.5 I topped up waited a few mins and still reads the same. Dumped some water and the same again.
derrick thomas avatar image derrick thomas adamr100 commented ·
Red wire of the sensor needs to be connected to either a +voltage source (same source as the main battery) or to one of the tank140 Vout(channel 1 to 4). Channels 1 and 2 Vout are only supplied when there is a voltage source connected to the vin ext. Power(left side of the tank 140). If you are using the tank140 to supply power to the sensors without connecting a power source to ext. Power input, you MUST use channel 3 or 4. The black wire from the sensor connects to In of the appropriate channel. The sensor you have linked to does NOT use a ground. There should be nothing connected to the ground terminal of the tank140 channel input. That is used for voltage sensors.
derrick thomas avatar image derrick thomas derrick thomas commented ·
Also check the update frequency in the tank setup menu. I would set it to 5 to 10 seconds.