Wich Victron devices need a type B RCD?
I have read many updated manuals from your web and there might be some contradictions.
In devices such as Quattro, Multiplus and Multiplus II there is nothing about type A or B RCDs, only the sentence:
"An earth leakage circuit breaker and a fuse or circuit breaker rated to support the expected load must be included in series with the output".
While in MultiGrid and EcoMulti there is the sentence:
"This product can cause a d.c. current in the external protective earthing conductor. Where a residual current-operated protective (RCD) or monitoring (RCM) device is used for protection in a case of direct or indirect contact, only an RCD or RCM of Type B is allowed on the supply side of this product".
Thank you!
MultiPlus Quattro Inverter ChargerMultiplus-IImultigrid
Dangermouse avatar image
Hi Just for info I found this website useful when selecting RCD types it might help you.
https://www.hager.co.uk/news-exhibitions-case-studies/18th-edition/selection-of-type-of-rcd/90066.htm
1 comment Share
Anil Ghatikar avatar image
I had enough trouble with spurious trippings on my 5 KVA x 3 setup with both Type A and Type AC I had also a high amount of electronics load on the ouput - All LED bulbs, multiple AV systems and around 55 IOT devices with inverter type Air conditioners
Changing to Type F from ABB( AC out 1) and Type Si from Schinder ( AC out 2) solved all the problems
Share
JohnC avatar image
Victron themselves provide a Chint NL1 in their 5kVA Easysolar box. Seem to be a Type A.
Share
kai avatar image
fwiw I used a RCD type A for my multiplus. Cost of type B here in Australia is exorbitant, last time I checked. It was close to the cost of the multiplus.