Richard Weir avatar image
Richard Weir asked
Multiplus 2 Aux relay working off SOC
My Aux relay is only giving out 50v when the it is closed, it should be 230v as is the input. It’s there to control a central heating circulation pump which runs when the heat pump is running which runs when SOC is >15%. But today it’s not working, just giving out 50v which is not enough to run the 230v pump
Multiplus-IIaux
Richard Weir answered ·
Wiring and state of the system with >15% SOC
Alexandra avatar image
Alexandra answered ·
@Richard Weir
Were you running the load direct off the aux relay? Or passing it through a contactor?
Max through the aux is 4Amps at 230v, see foot note 5 in the tech specs.
It’s on a 3a circuit and only running a small circ pump which takes minimal load.
Since I have 2 Multis working in parallel, I set up the other w multi with a generator start assistant without realising that it was already working in parallel. Anyway after relearning all the parallel multi stuff again I just wired my circuits through the slave relay and it works again. I’m pretty sure there is a fault with the Master multi relay which cause the problem in the first place.
MultiPlus-II Product page
MultiPlus-II Manual
MultiPlus-II 230V Datasheet
VE.Bus Error codes