Write swith state with modbus

I have Venus OS installed on a raspberry pi. And another raspberry with Home assistant.

I have managed to read parameter and write to modus register 22 (Active current limit)

However, when trying to write to "swith position" adress 33 Id does not work.

I read from adress 33 whithout a problem but writing a 2 or 3 for example does not work..

home assistant
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

It is working pretty well for me:
1677239602797.png

Have tried to use a Modbus tool to test? As you can see I have used "Modbus Mechanic" to write a "2" to register 33 and it has responded correctly by "Inverting". Using a tool would help to verify if the Victron end is working or if it's a configuration problem in HA.


1677239602797.png (63.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

arne999 avatar image
arne999 answered ·

I found the problem. I found a "inverter/charger toggle" in the VRM settings and turns it on (noticed the warning...) Anyway now it works!!