I have 3 x Multiplus II 48/3000 with 2 x 16 x 280 Ah LiFePO4.
I use this only as a ESS for buying in hours when the electricity is cheap (and then charge the cells) en sale in hours when prices are high (and then discharge the cells).
I stay within the healthy ranges of my cells (SOC >= 15% and SOC <=95%)
My average load is 4,5 kW for charge and discharge (every Multiplus takes 1,5 kW)
During charging the battery current is about 38 A, during discharge about -48 A.
I have calculated my AC round trip efficiency(RTE) in the month december 2022:
  • import from grid: 608 kWh
  • export to grid: 474 kWh
  • RTE = 474/608 = 78%
Import and export quantities are measured by Multiplus/gx (grid meter is still in backorder)
My questions are:
  • is 78% a normal quantity (I hoped this was 85%)?
  • if not: where should I look for errors and mistakes in my configuration to improve my efficiency?
Thanks in advance!
Multiplus-IIgrid parallel
Rob Duthie avatar image Rob Duthie commented ·
Hi
Be about right at 80% if the 3x inverters are in parallel the losses are much greater, Also the internal meters are not that accurate.
Also it depends on the PF of the loads can make difference.
shaneyake avatar image
shaneyake answered ·
Your RTE sounds about right to me.
90% AC to DC and DC to AC is what I see on average.
97% for the battery.
So 100*0.90*0.97*0.9 = 78.57% RTE