Since 1.4.2022 I was in island mode by setting multiplus to inverter mode.
13.9.2022 I switch multiplus from inverter to ON and system not working propertly
Before 1.4.2022 I use ESS whitout any problem more than 2 years.
System looks like don't know what to do and is confused. He floating between feeding to grit (this is not allowed) and charge from grid.
https://www.youtube.com/watch?v=vNwizu5_O5k
I am completely at a loss what happen.
I upgraded firmware multiplus II
I reset all and setup as new.
I try ET340 change for ET112
I try run only one mutliplus (no parallel)
When I setup in ESS grid metering inverter/charger, system start charging battery despite is not discharge below ess threshold and gradually stop using solar energy
When I setup in ESS grid meter external meter, system looks like in video.
What I noticed on the multiplus II don't show input current, but show input power
System
My system is:
2 x Multiplus II in parallel
ET340
1 x MTTP 250/100
1 x MTTP 250/100 ve.can
BMV-712
CCGX
MultiPlus Quattro Inverter ChargerESS
marekp avatar image
marekp answered ·
@Duto69
Is your system single phase?
What type battery you have?
Why Minimum SOC you have set to 90%?
I observed that "battery life" works up to 85% SOC but my minimum SOC is set to 20%.
When "Active SOC limit" gets set to 90% battery there will be not much use of battery by the system.
You have the ET340 but in your setup you have "grid mettering" done by "inverter/charger", why?
This zero current on AC-in can be caused by faulty CT socket on MP-II.
Try to clean this socket by plugging and unplugging 3.5mm plug in to the CT socket couple of times.
duto69 avatar image
duto69 answered ·
Yes, system is single phase
battery is AGM
SOC 90% because better life span
When I use ET340 system is totaly unstable, see in video
MP-II have internal CT
I don;t have external CT
marekp avatar image
marekp answered ·
@Duto69
If this is single phase system, why did you install ET340 and not ET112?
There is no point of using "battery life" if the "Minimum SOC" is set to 90%.
System could be unstable when unused CT socket in MP-II is faulty.
When this happens the internal CT is disconnected and system does not know how to calculate power flow through MP-II and all kinds of weird things happen.
New MP-II design does not have this round CT socket anymore. They use terminals now.
(what video you want me to see?)
duto69 avatar image
duto69 answered ·
Fault found, internal CT not work, thats all...
If I cancel parallel system, one multis work, second not.
That the reason, why in inverter mode work everything fine.
But I suppose, when I have external grid meter, internal is not use...
marekp avatar image marekp commented ·
@Duto69
Even if you use external Power meter, internal CT is also used to calculate AC loads and Critical loads.
The internal CT is not used only when you plug external CT into the socket.