I'm occasionally getting MPPT state 245. I can't find it defined anywhere in the doco. Does anyone know?
I'm occasionally getting MPPT state 245. I can't find it defined anywhere in the doco. Does anyone know?
Hey! I do not have an official answer for you. But I'm seeing this too and I have noticed that this only happens under the following circumstances:
So I am guessing this is kind of a "pre-start" or "calibrating" state right after the panels supply enough energy (threshold) for the charger to start but before actual charging begins.
For completeness' sake the full list:
State | Meaning |
0 | Off |
2 | Fault |
3 | Bulk |
4 | Absorption |
5 | Float |
6 | Storage |
7 | Equalize |
245 | Pre-Charge / Calibrating? |
252 | ESS |
As per the documentation of the ve.direct hex protocol "Device state values (register 0x0201)" state 245 means "The device is about to start (signal to external control)".