Multiplus II GX 5000 SOC jumping to 100% with no reason , batteries nowhere near full

soc-2.jpg



soc-1.jpg

As per title , this happens at least once a week from what I can tell.



This morning , it has just jumped from 73% to 100% , solar PV only just started kicking in , system voltage is way below still at 53.80 volts , absorbtion is set for 55.70 on MPPT controllers and in Multiplus is set to assume 95% SOC at 55.70 volts.


Any ideas?


I have just downloaded the data in excel where it confirms this as well.


Please see attached screenshots

SOC
soc-1.jpg (87.4 KiB)
soc-2.jpg (109.2 KiB)
soc-3.jpg (196.6 KiB)
soc-4.jpg (188.3 KiB)
16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
You forgot to include a screenshot of the inverters general tab, regarding SOC settings.
0 Likes 0 ·
teloth avatar image teloth klim8skeptic ♦ commented ·

I did not forget , as I already put that information in original message , " Multiplus is set to assume 95% SOC at 55.70 volts. " ie. state of charge when bulk is finished = 95%

0 Likes 0 ·
marekp avatar image marekp commented ·

Are you using "2 signal BMS" assistant or ESS with this settings set in it?

0 Likes 0 ·
teloth avatar image teloth marekp commented ·
I am not running ESS or any assistants.
0 Likes 0 ·
marekp avatar image marekp teloth commented ·
What battery you have?
0 Likes 0 ·
teloth avatar image teloth marekp commented ·
LifePO4 480Ah , not connected in any "clever" way like CANbus or anything.


State of charge is purely determined by Absorbtion voltages , in Multiplus , after the bulk finished. It works perfectly fine most of the time, but this phenomenon occurs once a week or so and it messes up SOC.


After 2 hours ago it happened this morning , it is obviously still showing me 100% SOC , luckily it is going to be an OK day today to truly hit 100% , but if it was a winters day , it will falsely claim 100% early in the morning , when in reality the SOC could be 70% for example and it will never reach where it is supposed to be. So I will go into the night thinking batteries are 100% , where they obviously are not.
0 Likes 0 ·
marekp avatar image marekp teloth commented ·

@Teloth

Voltage is not the best way to measure the SOC of the LFP battery.

If you want the SOC properly measured use SmartShunt or BMV.

BTW.

If you do not have a "clever" or other method of signaling to your chargers that the LFP battery cannot be charged or discharged for any reason, your battery will not last long.

You can of course relay on internal BMS (if it has one) that have a way to disconnect the battery from chargers/loads, but it is very poor way.

0 Likes 0 ·
teloth avatar image teloth marekp commented ·

I will have to disagree for the most part.

The reason I don't want any " clever " method is not to overcomplicate things unneccessarily.

There is one and ONLY thing can and does determine state of charge in my setup.

The figure is set in black and white in Inverter settings as " state of charge when bulk is finished = 95% "

So , when batteries reach 55.7 volts , whatever the current reading of SOC , this changes to 95% , which is what supposed to happen and works like this , as it should , most of the time.

But , this issue occurs in random timeframes , not exactly sure how often , but probably once a week or once in 2 weeks.

SO , this is clearly a glitch , out of the blue for SOC to jump to 100% , when it is NOWHERE near absobtion voltage.

MPPT chargers are all Victron , and they have clear parameters to what voltage they will charge the batteries up to, this is " clever " enough for me.

Have been running this system over a year , works great , apart from this weird issue.

All things you are talking about have nothing to do with help understand the reason " jump " of the SOC to 100% nor they can have any effect on this.

There are different ways to skin a cat. I don't need or want Smartshunt or BMV as both of these are within a degree of accuracy is already integrated in Multiplus II.

PS , of course I have a BMS on my battery banks , with cutoff etc. voltages set ...

That also has nothing to do with the reason for the SOC jump , as they cannot dictate what Multiplus shows me as SOC.

I appreciate you may be trying to help , but I think you should look at exactly what I am reporting , rather than diverging into irrelavant things.


1 Like 1 ·
marekp avatar image marekp teloth commented ·

@Teloth

Did you consider the internal resistance (IR) of your cells?

Battery voltage is directly related to IR under load or charge.

Same with temperature and its influence on the IR.

To be able to measure SOC based on voltage of the battery, it has to be disconnected from load or charge for couple minutes.

Also IR is getting higher as battery ages.

Method that you are using is good for Lead Acid battery.

You can do whatever you want with your battery. After all it is your battery.


1 Like 1 ·
Meine_Energiewende avatar image Meine_Energiewende marekp commented ·
fully agree .... you have to take care of lifepo4 or they wont last long.
0 Likes 0 ·
teloth avatar image teloth Meine_Energiewende commented ·
...
0 Likes 0 ·
teloth avatar image teloth marekp commented ·
I am sorry but I truly think you do NOT understand what I amsking or saying here as again , you are coming up with irrelevant topics and replies.


My batteries are just fine.


If they were NOT , I would be having this issue every day.

They are fully balanced , Delta is never higher than 50mV even under hig load or high charge.


Please re-read what I am asking / describing , if you understand what it is , come back and make relevant comment.

Otherwise no need for you to send response.

Unless you want to boost your forum post count for brownie points with totally irrelevant replies.


-2 Likes -2 ·
marekp avatar image marekp teloth commented ·
plonk\
1 Like 1 ·
dc4me avatar image dc4me teloth commented ·
What is wrong with you people asking for help and responding with nasty comments? If they are not answering your question go somewhere else.
0 Likes 0 ·
teloth avatar image teloth commented ·

@mvader or other Victron Gurus , would you mind looking at this to see what might be causing the issue?

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ teloth commented ·
Get yourself a proper installer instead of arguing with people trying to help.

You won’t get any official help for batteries that aren’t on the compatible list.

Having lithium batteries without a bms or a properly setup shunt will just cause issues.

There are tons of topics here you can search for with all the information you need.

Its not a glitch, you just haven’t set it up right.

5 Likes 5 ·
1 Answer
snoobler avatar image
snoobler answered ·

Why are you complaining? You clearly don't care about actual battery SoC since you're using one that can't count the incoming current from the PV.

Contact your reseller for support.