cavitt avatar image
cavitt asked
Easysolar 24/3000/70-50 earthing issues
I have an Easysolar 24/3000/70-50 running at 230V 50Hz. I appear to have an earthing issue. Firstly i am an electrician so don't hold back with technical answers please. When i measure the voltages, i get the following; P & N 234V, P & E 92V, N & E 142V.It doesn't make any difference if the ground relay is open or closed. Is this just a phantom voltage and i can put a hard bridge between N&E (AC in is from a generator, so not earthed independantly) or is there something more serious going on.
EasySolar All-in-One
klim8skeptic avatar image
klim8skeptic answered ·
The ac input relay will close when the genset is connected, then the neutral-pe bonding relay in the multiplus will open. You need a neutral-earth bond in your genset.
cavitt avatar image
cavitt answered ·
Thanks for the answer. i agree that there should be a bond between N & E on the Genset side. However i have the problem while running off the PV panels regardless of the relay being open or closed....?
Without ac coming in, the ground relay should be closed. (Unless you have it programmed otherwise)
jc2010 avatar image
jc2010 answered ·
@Cavitt
I noticed that your N & E reading of 142 V summed with your P & E reading of 92 V equals your P & N reading of 234 V. Would this mean that a live conductor is shorted to earth somewhere in your system and this short is behaving as voltage divider with the center point on E & N somewhere between P & N ?
@Cavitt
Good point above. Panels cables should only be connected to the MPPT(through isolators etc.). Panel frames should be grounded.