jdalbora avatar image
jdalbora asked
MPPT 75/15 lights not turning on
Hello, I've just installed an MPPT 75/15 connected to 2 Victron AGM 130AH batteries for a 24V set up. I've got 4, 10W DC LED lights wired to the load section of the controller, and my solar panel is all hooked up. On the bluetooth app, solar and battery seems to be working fine, but I am having trouble getting the lights to go on. I'm hoping to set it up in "streetlighting" mode, but I really want to test the system without waiting around until it is pitch black as this is a commercial construction site and everyone leaves at 4:30pm. Can someone help me test whether my lights are working with the system?
Thanks!
MPPT ControllersStreetlight
wkirby avatar image
wkirby answered ·
What happens when you disconnect the PV? This will stimulate "pitch black".
jdalbora avatar image jdalbora commented ·
Good question, I did try that and it didn't work at first. But, when I unwired the 2 of the 3 lights in the circuit, all of a sudden the first light came on, closest to the charge controller. Then when I wired up the 2 other lights they all stayed on. However, once wired up and I tried to repeat the simulated night time it didn't work again.
Now, here is the weird part. I have 8 of these individual systems on 8 carports. On one of the systems I hadn't connected the ground wire yet to the battery enclosure because I was being lazy and it worked! Any ideas on that one?
jdalbora answered ·
Yep, I tried simulating dark, no luck. After two weeks working on this, it is abundantly clear that the load output function on these charge controllers simply does not work. And it wasn't just one controller, it didn't work on 7 out of 8 units. Major hardware failure, we won't be using Victron again, needless to say.
markus avatar image markus ♦♦ commented ·
Sad to read it doesn't work. What's your batteries voltage? Maybe it is too low for the load output to come active?
Regards,
Markus
wkirby avatar image wkirby ♦♦ markus ♦♦ commented ·
I'm now beginning to suspect that it might be the inrush current limiting kicking in and not allowing the load output to turn on.
In this instance it is likely to be a high capacitive load which some LED lamps can present. Although 40W on a 24V supply is like ~1.7A continuous, the inrush current could be quite high.
jdalbora avatar image jdalbora wkirby ♦♦ commented ·
I was worried about the same thing, but for two reasons I don't think that is the problem. 1) These controllers have a 15A load output, I don't think the inrush current on a 1.5A LED driver would exceed 15A or 10X operating amperage. 2) One of the controllers is working just fine with the exact same LED setup. Again, the overwhelming evidence is that there is a serious manufacturing defect going on in these units. Will never use again, I've already switched the entire setup to midnight solar with zero problems. Battery voltages are just fine.