screwdriversteve avatar image
screwdriversteve asked
Quattro 24/5000 UPS not functioning from Grid to inverter
Hello all,
I am new to the forum but not new to inverter equipment. I have recently replaced my older inverter on my boat with a Quatto 24/5000 with GX unit, MK3 and 2 x 100/30 solar chargers connected to 6X 200 W panels.
The difficulty I am having is the unit has a delay when switching from shore power to inverter. I loose the clock on my microwave and if I have any loads on they stop until the inverter picks them up. I have enabled UPS function as per below. am I missing something?
Up date.... it only happens during loads like the water maker or when the microwave is on. When there is very little load like PC it works fine.
Thanks Steve
ups
screwdriversteve answered ·
Solved!! I found a neutral buss that was not tied to the main buss so there was 85VAC floating on the neutral that was confusing the Quattro. Works as it should now.
soren-dynamicmill avatar image
soren-dynamicmill answered ·
Did you find any solution to this problem?