12/100 Smart Battery Protect Li-ion mode Shutdown Voltage

Hey there,

When a Smart Battery Protect 12/100 is set in Li-ion mode, the BMS controls the shutdown when the battery reaches a certain low voltage. I am using a Ve Bus BMS. When in Li-ion mode, Victron Connect disables the shutdown setting on the Battery Protect. Where and by which device is this 'low voltage' level determined? is it programmed somewhere, or does the VE Bus BMS just know this value?


thanks for your help!

Battery Protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@roachmon

It is the VE.Bus BMS that should control the Smart BatteryProtect via its remote on/off port (H signal). There is an example in the manual how to wire this up.

The BMS gets the signals from the lithium smart battery. The battery is where you set the limit (allowed-to-discharge cell voltage, pre alarm threshold and allowed-to-charge minimum temperature).