Lynx BMS connected via cables to Lynx Distributor

Since Lynx distributor and Lynx BMS connected together results too long for my installation, do you think it’s a problem to connect them through short cables so that I can place the BMS on a horizontal plane and the Distributor vertically?

BMS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@VBo

I see no reason why this shouldn't work.

But it is absolutely important to dimension the connecting cables sufficiently according to the maximum currents to be expected. The Lynx distributors can handle up to 1000A.

In addition, longer RJ10 cables may be required.