jm0278 avatar image
jm0278 asked
Multiplus-II AC Input Current Limit -> Per Leg or Total?
I've got a new installation connected to grid power. Does the AC Input Current Limit setting limit power on L1 and L2 individually or does it limit the total amount of power available for L1 and L2 combined?
TIA
Multiplus-IIcurrent limit
mattylight avatar image
mattylight answered ·
I came here for an answer to the same question. So far I've only been able to get the input current limit to function on L1 but not L2. Kinda defeats the purpose of the ICL. Have you found an answer in the 7 months since you posted?
derrick thomas avatar image
derrick thomas answered ·
You must have the 2x120? When connected to split phase the current limit is for each phase, L1 and L2, but power assist only applies to L1 so essentially the limit only really applies to L1 since you could theoretically pull more than the current limit on L2. When connected to single phase the MP2 will ignore input on L2, pass thru power on L1, and combine L1 and L2 outputs. Thus, the current limit will apply to L1 input only but L1 and L2 outputs combined.